I purchased a 20kw and looking for estimates to install. Are there any electricians that would be interested! Or can someone provide referrals?
A good electrician is going to have to look at what you have to hone down what you are going to need to do the job right.
Is it a Generac generator?? I'm going to assume your on Natural Gas. I found a cut sheet for a Generac and it list a 20KW as 18KW of output using NG. It specs a 90A CB and needs almost 300K BTU of gas. If you no longer need the spa panel and it was properly wired for a 70A breaker then it might be possible that it could be used and the transfer switch mounted close to the meter. 1/2'' even right at the meter is no where big enough for that generator. I'd guess your going to need a 1"
Yes it is setup from the factory to run natural gas, but is very easily converted to lp with included hardware. I've considered burying a large propane tank to provide true emergency power in case we lose all utilities.
The regulator is mounted in the generator box and it is a 1/2" npt inlet. The specs do show a minimum of 1" pipe but with the inlet being 1/2", how does that work?