220 electrical question

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

trekrok

Sharpshooter
Supporting Member
Special Hen Supporter
Joined
Mar 6, 2009
Messages
4,051
Reaction score
6,903
Location
Yukon, OK
So it's not important to match the load to the breaker so long as the breaker is big enough?

I won't do gfci, just used as an example of the type box I was envisioning - male plug to breaker to female. plug.
 

1911Sooner

Sharpshooter
Supporting Member
Special Hen Supporter
Joined
Jun 12, 2005
Messages
12,873
Reaction score
31,340
Location
West OKC
1730231051494.png
 

KOPBET

Duck of Death
Supporting Member
Special Hen Supporter
Joined
Jun 28, 2008
Messages
13,721
Reaction score
10,381
Location
N36º11.90´ W95º53.29´
So it's not important to match the load to the breaker so long as the breaker is big enough?

Right, sort of.

The load appliance will have a plug that must match the receptacle that is appropriate for the circuit including the wire and breaker (so you don't plug a 20A device into a 15A circuit.)

If I am not mistaken, by current code (NEC or local) you must have a GFCI device for every circuit in the garage for 120-250V receptacles 50A or less.
 

Nate08chevy

Marksman
Joined
Dec 18, 2017
Messages
38
Reaction score
44
Location
Ponca City
Code allows for a breaker suppling a welder to be oversized based on a percentage over the average amp draw for the welder. Which means the breaker could be already oversized for the wire. Just fyi.

Please verify wire size before continuing with whatever you do. If you didn’t put it in, people do some wonky stuff like 12 or 14 gauge wire on a 50 amp circuit

I vote for sub panel and designated breakers for each device. Verified with NEC inspector GFCI is NOT required in that application.
 
Last edited:

mtnboomr

Questionable Character
Special Hen
Joined
Jan 25, 2023
Messages
1,473
Reaction score
2,514
Location
MWC, OK
I am a retired journeyman electrician.

A breaker is sized not only to protect the wiring, but to handle amp inrush on startup without tripping.

While a welder or saw may say it requires a certain amount of amperage to operate correctly, that is the amount of amperage required to run the item with no load on it. On startup, or under a load, the amount of amperage need to run continuously will increase. That 17-amp saw will likely need a minimum of 25 amps to run under a load (you notice I said MINIMUM). Therefore, installing a 30-amp breaker is required.
 

montesa

Sharpshooter
Special Hen
Joined
Feb 3, 2006
Messages
4,811
Reaction score
5,034
Location
OKC
I am a retired journeyman electrician.

A breaker is sized not only to protect the wiring, but to handle amp inrush on startup without tripping.

While a welder or saw may say it requires a certain amount of amperage to operate correctly, that is the amount of amperage required to run the item with no load on it. On startup, or under a load, the amount of amperage need to run continuously will increase. That 17-amp saw will likely need a minimum of 25 amps to run under a load (you notice I said MINIMUM). Therefore, installing a 30-amp breaker is required.
But that also means it's fine to run his saw on his 50amp plug right? Because that will more than handle the saws amp draw.
 

Nate08chevy

Marksman
Joined
Dec 18, 2017
Messages
38
Reaction score
44
Location
Ponca City
But that also means it's fine to run his saw on his 50amp plug right? Because that will more than handle the saws amp draw.
In my opinion, no it isn’t fine. The breaker is rated too high to trip at the appropriate time for the saw if something were to happen. For example if it sucks in a shirt and binds the amp draw will have to exceed 50 amps to trip the circuit. Twice the amount needed to run it normally. Thermal overload or internal motor protection ignored
 

Latest posts

Top Bottom