Yes. There’s a 50, 30,and 20amp pre-wired receptacle base/box put together for RV use.
Pulling it through 2 90’s is tough. 3 90’s is not impossible, but run the risk of straining the wire and possibly compromising the insulation. A megger will verify after the pull.
 
Joined
Mar 3, 2019
Messages
1,518
Reaction score
5,063
Location
OKC
Feeling pretty confident it won’t be too hard once I got the wire ( 6/3 UF-B) and saw it passed fairly easy in some 1,25” PVC. I think I’ll be able to pull a length of conduit down the wire and then glue it together once in place. The 2 - 90’s will be at each end… again put in place over the wire before glueing. Just need some time to do it now. Weather and holidays not helping.
 