Generac requires a 500 gallon minimum LP tank for an air cooled generator and 1000 gallon minimum for a liquid cooled on new generator installations. A 500 holds 400 gallons of LP and a 1000 holds 800.
We tell every customer about the 30/30 rule before installing their generator. You will get line freezing due to inadequate pressure/condensation formation when the tank is below 30% liquid volume and the temperature is at or below 30 degrees f. In cold weather, you are basically limited to 280 gallons of useful fule in a 500 gallon tank and 560 in a 1000. This is why you often see the old timers warming their LP tank with weed burners are burn barrels. I don't have the balls to do that myself.
Get as much volume as you can (i.e. twin 1000's), or look into LP tank heat blankets.
We tell every customer about the 30/30 rule before installing their generator. You will get line freezing due to inadequate pressure/condensation formation when the tank is below 30% liquid volume and the temperature is at or below 30 degrees f. In cold weather, you are basically limited to 280 gallons of useful fule in a 500 gallon tank and 560 in a 1000. This is why you often see the old timers warming their LP tank with weed burners are burn barrels. I don't have the balls to do that myself.